Want put a basin to wash hands in the shed. I know there is a rule as to how close to a GPO a basin can be (600mm ?) but is it the same or different for a sub board? As the best place for the tub is close to one and three phase power?
We will start with this one
AS/NZS 3000:2007 Clause 6.204.6 - A switchboard shall not be installed within any classified zone
With a fixed water container not exceeding 45L in capacity with fixed taps you have 2 classified zones
Zone 0 - is the interior of the fixed water container ie the sink
Zone 2 - is the area surrounding the fixed water container. The area shall be limited by 0.15m on the vertical plane from the internal rim of the sink and the floor and 0.4m on the horizontal plane above the sink
I thought I read and can't find it again that also the switchboard would need to be suitably covered for splashing etc.
This items above are for information purposes only as there are other mitigating circumstances of an installation and its equipment that impact it.